>Thanks.  Someone else had suggested these, but unfortunately we've got a
>load of 70amp per circuit, so these don't cut it.
>
>Appreciate it tho.  I should've been more clear up front.


FUSE CAPACITY- .18 to 15 A per fuse
PANEL CAPACITY- 100 A (max.) per bus; 200 A total
OPERATING VOLTAGE- -48 VDC

So run 5 wires to the unit from 5 15A parallel circuits. That will give you 
your 75A and redundancy. It is a bit of a hack, but it should be fine. Just 
use the same gauge wire and fuses in all positions.

-Robert