> It was a power issue. You see, the location where the circuit terminates
> is a lumber mill. The electric power for the mill feeds to the mill then
> to the office where the router is located. The router was plugged into a
> standard small apc ups. Well, whenever the mill would startup, the
> voltage would drop down throughout the office - albeit slightly and only
> for a few seconds - which would cause the router to throw generate crc
> errors. It probably wouldnt have been noticed if this were a full t1 with
> 1.5 megabit of bandwidth but since there was only 256k, there wasnt much
> room for discarded packets or errored packets.
Oh, APC. There's your problem. ;-) Switch to the PowerWare
9100-series and you won't have that problem.
I'm glad you figured it out!