For reference from a couple of boxes we have:
system power redundancy mode = redundant
system power total = 3830.40 Watts (91.20 Amps @ 42V)
system power used = 2289.00 Watts (54.50 Amps @ 42V)
system power available = 1541.40 Watts (36.70 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-4000W-INT 3830.40 91.20 OK OK on
2 WS-CAC-4000W-INT 3830.40 91.20 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 FAN-MOD-9 241.50 5.75 OK
2 FAN-MOD-9 241.50 5.75 OK
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 OSM-2+4GE-WAN+ 213.36 5.08 213.36 5.08 on on
2 OSM-2+4GE-WAN+ 213.36 5.08 213.36 5.08 on on
3 WS-X6582-2PA 105.00 2.50 105.00 2.50 on on
4 OSM-1CHOC12/T3-SI 184.80 4.40 184.80 4.40 on on
5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
6 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
7 WS-X6582-2PA 105.00 2.50 105.00 2.50 on on
8 OSM-8OC3-POS-SI+ 142.80 3.40 142.80 3.40 on on
9 OSM-1CHOC12/T3-SI 184.80 4.40 184.80 4.40 on on
For reference From one of our more loaded boxes
And from another 6509
system power redundancy mode = redundant
system power total = 2331.00 Watts (55.50 Amps @ 42V)
system power used = 1272.60 Watts (30.30 Amps @ 42V)
system power available = 1058.40 Watts (25.20 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-2500W 2331.00 55.50 OK OK on
2 WS-CAC-2500W 2331.00 55.50 OK OK on
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6516-GBIC 142.80 3.40 142.80 3.40 on on
2 WS-SVC-FWM-1 171.78 4.09 171.78 4.09 on on
3 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
4 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
6 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
7 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
Regards,
Neil.
--
Neil J. McRae -- COLT
Neil.McRae at COLT.NET
> -----Original Message-----
> From: cisco-nsp-bounces at puck.nether.net [mailto:cisco-nsp-
> bounces at puck.nether.net] On Behalf Of Gert Doering
> Sent: 15 November 2006 21:55
> To: Simon Lockhart
> Cc: Church, Chuck; Gert Doering; Jay Ford; cisco-nsp at puck.nether.net
> Subject: Re: [c-nsp] power requirement for sup720 migration
>
> Hi,
>
> On Wed, Nov 15, 2006 at 09:15:09PM +0000, Simon Lockhart wrote:
> > On the 6503, slot 2 reserves enough power for you to plug in a 2nd
> Supervisor,
> > which is why it looks like the 6516 in that slot is using more power
> than the
> > other...
>
> Hmmm. Good point.
>
> (Anyone having -GBIC blades in *other* slots with differing power
> requirements?)
>
> gert
> --
> USENET is *not* the non-clickable part of WWW!
>
> //www.muc.de/~gert/
> Gert Doering - Munich, Germany
> gert at greenie.muc.de
> fax: +49-89-35655025 gert at net.informatik.tu-