On Tue, 22 Jul 2008, Teller, Robert wrote:

> I am in the process of installing two Cisco 6500 chassis and was curious
> what types of PDU's people are using.

Note that most of my stuff is not in areas with raised floors, so power 
and data usually need to feed in from the top of the cabinet/relay rack.

Right now, I'm just pulling two pairs of 208V/20A circuits in L6-20 
receptacles above the cabinet where the 6509 will be located.  One pair 
comes off of a generator-backed/line-conditioned emergency power panel and 
the other pair comes off of a UPS output panel.

I do use PDUs smaller gear that will live in the same cabinet and I 
normally feed these from 120V/30A circuit, presented as an L5-30 
receptacle above the cabinet.  I'll pull one of these from an emergency 
power panel and one from a UPS panel and drop a PDU from each into each 
cabinet, so single-powered boxes can be run from either and dual-powered 
boxes can be run from both normal/emergency and UPS power.

jms