[c-nsp] fabric switching enable
Hank Nussbacher
hank at efes.iucc.ac.il
Wed Jun 18 00:34:31 EDT 2008
On Tue, 17 Jun 2008, Pham, Loc wrote:
Another interesting command to explore is:
petach-tikva-gp#sho platfor hard capa fabr
Switch Fabric Resources
Bus utilization: current: 0%, peak was 8% at 09:10:06 IST Thu Feb 28
2008
Fabric utilization: Ingress Egress
Module Chanl Speed rate peak rate peak
1 0 8G 0% 3% @06:07 03Feb08 0% 15% @10:04
28Feb08
2 0 8G 0% 0% 0% 3% @06:43
03Feb08
3 0 8G 0% 3% @04:47 03Feb08 0% 7% @12:41
26Mar08
4 0 8G 0% 2% @17:01 17May08 0% 3% @21:58
03Feb08
7 0 20G 0% 12% @10:09 28Feb08 0% 6% @19:20
03Mar08
9 0 20G 0% 4% @12:32 03Feb08 0% 7% @16:13
11Feb08
9 1 20G 0% 3% @19:27 03Feb08 1% 11% @18:13
19Mar08
10 0 20G 0% 1% @10:41 09Feb08 0% 1% @05:57
03Feb08
10 1 20G 1% 6% @19:20 03Mar08 0% 7% @19:20
03Mar08
11 0 20G 1% 11% @10:51 12May08 1% 3% @11:23
27Mar08
Switching mode: Module Switching
mode
1
compact
2
compact
3
compact
4
compact
7
compact
9
compact
10
compact
11
compact
-Hank
> Thanks Pete : this is what I have
> sh fab sw
> Global switching mode is Flow through
> dCEF mode is not enforced for system to operate
> Fabric module is not required for system to operate
> Modules are allowed to operate in bus mode
> Truncated mode is not allowed unless threshold is met
> Threshold for truncated mode operation is 2 SFM-capable cards
>
> Module Slot Switching Mode
> 1 Bus
> 2 Bus
> 3 Bus <<<< can be
> --------------
>
> I read about cycle the power ;-) thanks for the head up....
> So I need to plan for a maint-window then. Since I have mix cards, I
> need to use truncate mode, right ?
>
> Regards,
> Loc Pham, # 17030 R/S
> "We switch our network dedicately :One packet at a time... "
>
> -----Original Message-----
> From: Peter Rathlev [mailto:peter at rathlev.dk]
> Sent: Tuesday, June 17, 2008 2:27 PM
> To: Pham, Loc
> Cc: Cisco NSPs
> Subject: Re: [c-nsp] fabric switching enable
>
> On Tue, 2008-06-17 at 12:35 -0700, Pham, Loc wrote:
>> How can I identify whether our module is switched on mix mode and how
>> to change it ? any gotcha ?
>>
>> xxx#sh fab sw mo all
>> Module Slot Switching Mode
>> 1 Bus
>> 2 Bus
>> 3 Bus
>>
>> XXX#sh fab sta
>> slot channel speed module fabric
>> status status
>> 1 0 20G OK OK
>
> You wouldn't happen to have a "fabric switching-mode force bus-mode" in
> your running config?
>
> Try doing a "show fabric switching-mode" without the "module all", it
> gives some interesting lines in the beginning.
>
> Changing switching mode power cycles the modules by the way. I guess
> that's a gotcha. :-)
>
> Regards,
> Peter
>
>
>
>
> _______________________________________________
> cisco-nsp mailing list cisco-nsp at puck.nether.net
> https://puck.nether.net/mailman/listinfo/cisco-nsp
> archive at http://puck.nether.net/pipermail/cisco-nsp/
>
More information about the cisco-nsp
mailing list