[c-nsp] rack power question
Tim Durack
tdurack at gmail.com
Sat Mar 22 22:27:59 EDT 2008
For a 6509-V-E with 2xVS-S720-10G-3CXLs and 7xWS-X6708-10G-3CXL.Cisco
Power Calculator shows:
107.76 Amps 4525.92 Watts 18183.55 BTU/Hr
At 21u you could squeeze two in a rack, for 9K (we aren't planning on
doing that though.)
On the server side something like an HP C Class Blade Chassis with 16
blades can hit 3K when the fans rev up.
At 10u you could squeeze 4 in a rack, but cooling is going to be an
issue. With enclosed ducted racks, we currently have plans to put 3 in
a rack for a total of 9K.
So yes we could require >6K.
Tim:>
On Sat, Mar 22, 2008 at 10:02 PM, Patrick Giagnocavo <patrick at zill.net> wrote:
>
> Hopefully this classifies as on-topic...
>
> I am discussing with some investors the possible setup of new datacenter
> space.
>
> Obviously we want to be able to fill a rack, and in order to do so, we
> need to provide enough power to each rack.
>
> Right now we are in spreadsheet mode evaluating different scenarios.
>
> Are there cases where more than 6000W per rack would be needed?
>
> (We are not worried about cooling due to the special circumstances of
> the space.)
>
> Would someone pay extra for > 7KW in a rack? What would be the maximum
> you could ever see yourself needing in order to power all 42U ?
>
> Cordially
>
> Patrick Giagnocavo
> patrick at zill.net
>