On Fri, May 23, 2008 at 11:51:30AM +0100, A.L.M.Buxey at lboro.ac.uk wrote:
> Hi,
>
> > We running different power supplies on one of our 6509 for years,
> > no problems with that configuration:
>
> yes, you just need to be very careful that your blades dont
> draw too much power for the one not in use. eg if you are currently
> on a 2500W supply...and that fails , leaving you with only
> a 1300W then your blades may take too much for that and thus some
> will fail.
Yes, I should note that this system is old one, Sup2 based,
with old fans, using only 584.22 Watts, so even when we lose
AC power - 1300Watt DC power supply provides enough power to run.
> eg in the scenario posted...
>
> > Switch#show power
> > system power redundancy mode = redundant
> > system power total = 2331.00 Watts (55.50 Amps @ 42V)
> > system power used = 584.22 Watts (13.91 Amps @ 42V)
> > system power available = 1746.78 Watts (41.59 Amps @ 42V)
>
> so, system thinks its got 1746 available.... and 2331 supplied..
> however:
>
> > PS Type Watts A @42V Status Status State
> > ---- ------------------ ------- ------ ------ ------ -----
> > 1 WS-CDC-1300W 1153.32 27.46 OK OK on
> > 2 WS-CAC-2500W 2331.00 55.50 OK OK on
>
> that 1300W wont provide enough if the power used was eg 1341.55 Watts
> as the system THINKS its got 2500....