andrew2 at one.net wrote:
> I'm getting ready to install some RPS 675's in order to dual cord some
> 3750's and ran across this in the manual:
>
> "Do not use different power sources to power up the RPS and the connected
> device. If you connect to separate AC power sources, reset conditions might
> occur."
>
> Huh? My intent is to plug the RPS into a different PDU than the actual
> switches so that the switches can stay online in the event of a power
> failure on their primary circuit. Is this Cisco FUD or are there good
> reasons I wouldn't want to plug an RPS into a different circuit than the
> connected switches?
The only possible problem that I can foresee is the potential to create
a ground loop. That wouldn't be good. The RPSs are only meant to
protect against a power supply failure, not a power source failure.
That said, I use a RPS 675 in the same way that you're describing
without any problems.
Also, remember that the RPS 675 can only keep 1 connected device powered
up in the event of a power failure. The RPS 2300 can do 2. Ie, if you
have a stack of 4 switches with 2 connected to circuit A, 2 connected to
circuit B, the RPS connected to circuit C (with all 4 switches connected
to that RPS) and circuit B fails, only 1 of the 2 switches connected to
circuit B will get power from the RPS. The other will be dead in the water.
Justin