Hi Bill,

It all depends on what other modules you have installed in your chassis.  I am running a 6509-E with 3000W power supplies using 110v, however I have to run them in combined mode.  To give you some real-time data here's the output from my 'sh power':

system power redundancy mode = combined
system power total =     1952.16 Watts (46.48 Amps @ 42V)
system power used =      1275.54 Watts (30.37 Amps @ 42V)
system power available =  676.62 Watts (16.11 Amps @ 42V)
                        Power-Capacity PS-Fan Output Oper
PS   Type               Watts   A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1    WS-CAC-3000W       1171.38 27.89  OK     OK     on 
2    WS-CAC-3000W       1171.38 27.89  OK     OK     on 
                        Pwr-Allocated  Oper
Fan  Type               Watts   A @42V State
---- ------------------ ------- ------ -----
1    WS-C6509-E-FAN      150.36  3.58  OK
                        Pwr-Requested  Pwr-Allocated  Admin Oper
Slot Card-Type          Watts   A @42V Watts   A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1    WS-X6516A-GBIC      152.04  3.62   152.04  3.62  on    on
2    WS-X6148-RJ-45      100.38  2.39   100.38  2.39  on    on
3    WS-X6148-RJ-45      100.38  2.39   100.38  2.39  on    on
4    WS-X6148-45AF       107.94  2.57   107.94  2.57  on    on
5    WS-SUP720-BASE      315.00  7.50   315.00  7.50  on    on
6    (Redundant Sup)       -     -      315.00  7.50  -     -
                        Inline         Inline         Inline         Inline
                        Pwr-Requested  Pwr-Allocated  Local-Pwr-Pool Power
Slot Card-Type          Watts   A @42V Watts   A @42V Watts   A @42V Status
---- ------------------ ------- ------ ------- ------ ------- ------ ----------
4    WS-F6K-FE48-AF        -     -        -     -       34.61  0.82  On


Have a good day,
  Aaron

-------------
Aaron Childs
Assistant Director, Networking
Westfield State College
http://www.wsc.ma.edu/it/

-----Original Message-----
From: cisco-nsp-bounces at puck.nether.net [mailto:cisco-nsp-bounces at puck.nether.net] On Behalf Of Bill Blackford
Sent: Tuesday, May 26, 2009 1:52 PM
To: cisco-nsp at puck.nether.net
Subject: [c-nsp] Cat 6509 Power supplies

I have a question about power supplies.

I am upgrading a 6509 chassis from SuP1/MFSC2 to a pair of SUP720-3BXL's, fan and new power supplies. I originally spec'd a pair of 4000W units. Now as we know, these can only support NEMA L6-30, vs. the variable power supplies such as the 3000W. I've run out of L6-30R's in my data center as our new rack PDU's are of this spec. I may need to use 110V NEMA 5-20 plugs.

Can the 3000W power supply (in redundant mode) support a fully populated 6509 chassis (no POE) when using 110VAC?

Thanks



--
Bill Blackford                     
Senior Network Engineer            
Technology Systems Group           
Northwest Regional ESD             

my /home away from home


_______________________________________________
cisco-nsp mailing list  cisco-nsp at puck.nether.net
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/


More information about the cisco-nsp mailing list