Chuck,
We were in the same situation in one of our data centers and we installed a PECO II power system. The cabinet we have holds 3 50AMP rectifiers (we have it configured for N+1 so we get 100AMPs out of the cabinet and redundancy). You can also expand the main cabinet with another rectifier cabinet for a total system capacity of 200-300AMPs depending on how you have it configured. Even though this is run through two of our AC UPS's we still installed DC batteries for good practice.
---Chris
On Mar 29, 2010, at 3:36 PM, Charles Mills wrote:
> Is anyone running DC for their Cisco 6509's and just using rack mount
> DC inverters in lieu of having a DC Power Plant?
>
> And..if so, what's everyone using for their inverters? Any to avoid
> or to recommend?
>
> Chuck