On 9/22/10 1:31 PM, Peder wrote:
> Does anybody have a good rule of thumb as to what type of coax to use for
> DS3 over various distances? I know it has to be 75ohm, but have read it can
> be RG-59 or RG-6. Also, on the RG-59 I have seen solid core and braided.
> We have to run a cable about 250' to the telco equipment thru a messy
> ceiling, so we only want to do it once with the correct cable. In the lab,
> we just use cheap RG-59 but I don't know if it will have issues over a
> distance of 250'. Thanks.
I would recommend 734 type cable which is designed for DS3. It is
similar in size to RG-59 but made to better tolerances than you're
likely to find in RG-59. It's available in figure-8 twin configuration
specifically for DS3 transmit/receive.
The cable you'll typically find these days sold as RG-59 is designed for
TV distribution and often has copper-clad steel center conductor instead
of pure copper as well as aluminum foil shield with drain wires instead
of copper braid. Terminating this stuff with BNC connectors is a pain.
It's designed for the F-type connectors used in cable TV.
Also ensure that you use 75-ohm BNC connectors. The insulator is shaped
differently than the normal 50-ohm type commonly available.
--