[c-nsp] Power Consumption OID
Ryan West
rwest at zyedge.com
Mon Mar 28 08:48:42 EDT 2011
The following MIB should work for the 7606, but since the 3750 is fixed, I'm not sure you'll be able to extract the information via SNMP.
snmpwalk 4510E 1.3.6.1.4.1.9.9.117.1.1.1
CISCO-ENTITY-FRU-CONTROL-MIB::cefcPowerRedundancyMode.15 = INTEGER: redundant(2)
CISCO-ENTITY-FRU-CONTROL-MIB::cefcPowerUnits.15 = STRING: centiAmpsAt12V
CISCO-ENTITY-FRU-CONTROL-MIB::cefcTotalAvailableCurrent.15 = INTEGER: 18333
CISCO-ENTITY-FRU-CONTROL-MIB::cefcTotalDrawnCurrent.15 = INTEGER: 10766
CISCO-ENTITY-FRU-CONTROL-MIB::cefcPowerRedundancyOperMode.15 = INTEGER: redundant(2)
18333 * 0.01 * 12 = 2199.66
10766 * 0.01 * 12 = 1291.92
4510E#show power
Power Fan Inline
Supply Model No Type Status Sensor Status
------ ---------------- --------- ----------- ------- -------
PS1 PWR-C45-6000ACV AC 6000W good good good
PS1-1 220V good
PS1-2 220V good
PS2 PWR-C45-6000ACV AC 6000W good good good
PS2-1 220V good
PS2-2 220V good
Power supplies needed by system : 1
Power supplies currently available : 2
Power Summary Maximum
(in Watts) Used Available
---------------------- ---- ---------
System Power (12V) 1292 2200
-ryan
From: Mohammad Khalil [mailto:eng_mssk at hotmail.com]
Sent: Monday, March 28, 2011 4:40 AM
To: Ryan West; cisco-nsp at puck.nether.net
Subject: RE: [c-nsp] Power Consumption OID
Hi
yes that what i am looking for , but the OIDs does not exist for my devices such as 7606S and ME3750
> From: rwest at zyedge.com<mailto:rwest at zyedge.com>
> To: eng_mssk at hotmail.com<mailto:eng_mssk at hotmail.com>; cisco-nsp at puck.nether.net<mailto:cisco-nsp at puck.nether.net>
> Subject: RE: [c-nsp] Power Consumption OID
> Date: Sun, 27 Mar 2011 17:34:24 +0000
>
> Is this what you're looking for:
>
> ftp://ftp.cisco.com/pub/mibs/v2/POWER-ETHERNET-MIB.my
>
> 3560:
> snmpwalk test1-sw1 .1.3.6.1.2.1.105.1.3.1.1.2
> POWER-ETHERNET-MIB::pethMainPsePower.1 = Gauge32: 370 Watts
> snmpwalk test2-sw1 .1.3.6.1.2.1.105.1.3.1.1.4
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.1 = Gauge32: 189 Watts
>
> 4510E
> snmpwalk test2-sw1 .1.3.6.1.2.1.105.1.3.1.1.2
> POWER-ETHERNET-MIB::pethMainPsePower.1 = Gauge32: 1550 Watts
> POWER-ETHERNET-MIB::pethMainPsePower.2 = Gauge32: 1550 Watts
> POWER-ETHERNET-MIB::pethMainPsePower.3 = Gauge32: 800 Watts
> POWER-ETHERNET-MIB::pethMainPsePower.4 = Gauge32: 800 Watts
> POWER-ETHERNET-MIB::pethMainPsePower.7 = Gauge32: 800 Watts
> POWER-ETHERNET-MIB::pethMainPsePower.8 = Gauge32: 800 Watts
> snmpwalk test2-sw1 .1.3.6.1.2.1.105.1.3.1.1.4
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.1 = Gauge32: 6 Watts
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.2 = Gauge32: 11 Watts
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.3 = Gauge32: 0 Watts
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.4 = Gauge32: 0 Watts
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.7 = Gauge32: 30 Watts
> POWER-ETHERNET-MIB::pethMainPseConsumptionPower.8 = Gauge32: 3 Watts
>
> -ryan
>
> -----Original Message-----
> From: cisco-nsp-bounces at puck.nether.net<mailto:cisco-nsp-bounces at puck.nether.net> [mailto:cisco-nsp-bounces at puck.nether.net]<mailto:[mailto:cisco-nsp-bounces at puck.nether.net]> On Behalf Of Mohammad Khalil
> Sent: Sunday, March 27, 2011 10:45 AM
> To: cisco-nsp at puck.nether.net<mailto:cisco-nsp at puck.nether.net>
> Subject: [c-nsp] Power Consumption OID
>
>
> i am trying to find an OID for power consumption ? is there a way to extract these information?
>