[c-nsp] C6k power reserved for redundant sup?
Peter Rathlev
peter at rathlev.dk
Mon Jul 2 14:00:58 EDT 2012
So there I was, just having OIR-inserted an extra WS-X6708-10GE in one
of our existing core switches. But it didn't boot up because we don't
have enough juice. :-( We should of course just install large PSUs
(replacing WS-CAC-3000W) but it'll take some time to order these.
Looking at the output from "show power" I can see that the box reserves
328.44 W for a redundant supervisor. We have no intention of ever
placing an extra supervisor in this box, but I can't see how to avoid
this reservation. Would anybody here know of a way to do that?
It runs SXI1 AIS and the log message when inserting the module was:
005641: Jul 2 16:54:45.578 CEST: %C6KPWR-SP-4-POWERDENIED: insufficient power, module in slot 8 power denied.
The output from "show power":
system power redundancy mode = redundant
system power total = 2771.16 Watts (65.98 Amps @ 42V)
system power used = 2381.40 Watts (56.70 Amps @ 42V)
system power available = 389.76 Watts ( 9.28 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-3000W 2771.16 65.98 OK OK on
2 WS-CAC-3000W 2771.16 65.98 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 WS-C6509-V-E-FAN 252.00 6.00 OK
2 WS-C6509-V-E-FAN 252.00 6.00 OK
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
2 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
4 WS-X6724-SFP 125.16 2.98 125.16 2.98 on on
5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
6 (Redundant Sup) - - 328.44 7.82 - -
8 WS-X6708-10GE 444.36 10.58 - - on off (FRU-power denied)
9 WS-X6708-10GE 444.36 10.58 444.36 10.58 on on
Trying to power down module 6 fails:
SomeSwitch(config)#no power enable module 6
%Error: nonexistent FRU
SomeSwitch(config)#
Thanks a bunch for any pointers. The box is too critical to use combined
powering by the way.
--
Peter