[cisco-voip] CallManager 7.1(3) on MCS7835I3-K9-CMC2
Jason Aarons (US)
jason.aarons at us.didata.com
Wed Jun 2 09:14:58 EDT 2010
Cool. Syslog from RTMT had the details. Surprised this was in the Alert Central section of RTMT! -jason
Can IBM Director poll/manage MCS-7835I3 ? If customer wants to monitor hardware/raid/temps, etc? I'm asking are the IBM snmp/mibs on the RedHat platform appliance in 7.1(3).
Jun 1 19:18:44, USAvp4221IRVG01, Critical, Director Agent, : IBMPSG_TemperatureEvent USAvp4221IRVG01 Temperature Sensor 2 exceeded the manufacturer defined threshold of 45 Celsius. The current value is 41 Celsius. Sev: 6., 33285
Jun 1 19:18:49, USAvp4221IRVG01, Notice, messagebus, : messagebus -TERM succeeded, 33286
Jun 1 19:18:49, USAvp4221IRVG01, Notice, cimlistenerd, : Shutting down Pegasus CIM Listener , 33287
Jun 1 19:18:49, USAvp4221IRVG01, Notice, cimlistenerd, : succeeded, 33288
Jun 1 19:18:49, USAvp4221IRVG01, Notice, cimlistenerd, : [60G, 33289
Jun 1 19:18:49, USAvp4221IRVG01, Notice, rc, : Stopping cimlistenerd: succeeded, 33290
Jun 1 19:18:50, USAvp4221IRVG01, Warning, cimserver[6243], : /opt/ibm/icc/cimom/lib, 33291
Jun 1 19:18:54, USAvp4221IRVG01, Info, cimserver[2289], : PGS10031: CIM server CIM Server stopped., 33292
Jun 1 19:18:56, USAvp4221IRVG01, Notice, cimserverd, : succeeded, 33293
Jun 1 19:18:56, USAvp4221IRVG01, Notice, icesnmp, : stopdirsnmpd startup succeeded, 33294
Jun 1 19:19:21, USAvp4221IRVG01, Notice, twgend, : Requesting service to end., 33295
Jun 1 19:19:21, USAvp4221IRVG01, Notice, twgend, : Waiting for service to end., 33296
Jun 1 19:20:01, USAvp4221IRVG01, Notice, twgend, : getnameinfo failed, 33297
Jun 1 19:20:01, USAvp4221IRVG01, Notice, twgend, : Service ended., 33298
Jun 1 19:20:01, USAvp4221IRVG01, Notice, twgagent, : twgend startup succeeded, 33299
Jun 1 19:20:02, USAvp4221IRVG01, Notice, servm, : servM shutdown failed, 33300
Jun 1 19:20:02, USAvp4221IRVG01, Notice, sshd, : sshd shutdown succeeded, 33301
Jun 1 19:20:02, USAvp4221IRVG01, Info, snmpd[3589], : Received TERM or STOP signal... shutting down... , 33302
From: Jason Aarons (US)
Sent: Wednesday, June 02, 2010 7:26 AM
To: cisco-voip at puck.nether.net
Subject: CallManager 7.1(3) on MCS7835I3-K9-CMC2
Customer Data Center lost power, then lost AC so it go hot in there!
I suspect that CallManager 7.1(3) on MCS7835I3-K9-CMC2 got hot enough to where the BIOS protected the machine by shutting it down. Since it wasn't a power outage I don't think the BIOS would re-start the hardware but rather keep it shut down and wait for a manual restart. If your engine is overheating you wouldn't want it to keep restarting, you want to protect it right?
Customer tested that during a power down/up scenario the MCS7835I3-K9-CMC2 would reboot and stay running, but I don't want to "test" a high heat situation. Is there any way to confirm what the expected behavior is when a IBM server (is the MCS-7835I3 actually a IBM x3650-M2) overheats? What is the temp threshold the hardware shuts down, etc.
-----------------------------------------
Disclaimer:
This e-mail communication and any attachments may contain
confidential and privileged information and is for use by the
designated addressee(s) named above only. If you are not the
intended addressee, you are hereby notified that you have received
this communication in error and that any use or reproduction of
this email or its contents is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify us immediately by replying to this message and deleting it
from your computer. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://puck.nether.net/pipermail/cisco-voip/attachments/20100602/3fc8f0e8/attachment.html>
More information about the cisco-voip
mailing list