[cisco-voip] UCS 5108 power requirements under full load

Chris Ward (chrward) chrward at cisco.com
Fri May 13 09:01:39 EDT 2011


I thought I remembered seeing in a UCS preso that the only time a UCS
actually "required" more than 1x PSU was when you put in a B440 or B230
since they support the Xeon x75XX processors.

 

I have a UCS in my lab with 8x B200M1 and one of the PSUs is in a
standby state leaving only 3 active. I also just took a look at UCS
manager and each of the 3 PSUs that are active are only drawing about
425W.

 

I think unless you are running all of the blades at 100% capacity and
100% CPU, 100% of the time, you probably won't see 10000W usage.

 

+Chris

Hosted Collaboration Solution TME

 

From: cisco-voip-bounces at puck.nether.net
[mailto:cisco-voip-bounces at puck.nether.net] On Behalf Of ciscozest
Sent: Friday, May 13, 2011 8:08 AM
To: cisco-voip at puck.nether.net
Subject: [cisco-voip] UCS 5108 power requirements under full load

 

I am new to UC on UCS and need some advise on the basic power
requirements for UCS 5108. We are going to use 8 x B200M2 servers (full
load) with 4 power supplies (2500W each) in single 5108 chassis and grid
redundancy mode is desired.
Does this mean we need to have 10000 watt power for fully loaded single
UCS 5108 system if not, what would be the best practice for this?
Your advise is much apreciated. 