[j-nsp] T4000 power architecture
Sam Silvester
sam.silvester at gmail.com
Wed Sep 10 18:36:49 EDT 2014
Hi Aqeel - thanks for the reply.
Agree 100% - the problem is, we only seem to be getting power to FPC0 from
one PEM... have a look below (and also note that FPC1 is fine, as are the
rest of the FPCs).
The question is - are we looking at a PEM fault here, or a midplane fault?
As per previous discussion, the FPC itself seems fine, as moving it to
another slot resolves the issue. Putting another card into slot 0 yields
the same result as below.
PEM 0 status:
State Online
Temperature 32 degrees C / 89 degrees F
DC Input: OK
Voltage(V) Current(A) Power(W) Load(%)
INPUT 0 54.750 4.312 236 9
INPUT 1 54.500 6.000 327 13
INPUT 2 54.625 11.750 641 26
INPUT 3 54.750 6.125 335 13
INPUT 4 54.250 10.500 569 23
INPUT 5 54.500 6.062 330 13
DC Output Voltage(V) Current(A) Power(W) Load(%)
FPC 0 55.062 8.625 474 31
FPC 1 55.250 4.062 224 14
<...snip...>
PEM 1 status:
State Online
Temperature 30 degrees C / 86 degrees F
DC Input: OK
Voltage(V) Current(A) Power(W) Load(%)
INPUT 0 54.500 3.250 177 7
INPUT 1 54.625 3.375 184 7
INPUT 2 54.500 12.437 677 28
INPUT 3 54.500 5.125 279 11
INPUT 4 54.625 12.062 658 27
INPUT 5 54.375 2.750 149 6
DC Output Voltage(V) Current(A) Power(W) Load(%)
FPC 0 0.000 0.000 0 0
FPC 1 55.125 4.500 248 16
<...snip...>
On Wed, Sep 10, 2014 at 8:48 PM, aqeel ahmed <aqeelpk at yahoo.com> wrote:
> Hi
>
> Though aimed for redundancy If system has both power supplies installed
> then it will automatically load balance and in case one power supply goes
> down then whole system will be on single power supply left working.
>
> For further details you can refer to following juniper document.
>
>
> http://www.juniper.net/techpubs/en_US/release-independent/junos/information-products/topic-collections/hardware/t-series/t4000/hwguide/t4000-hwguide.pdf
>
> Regards
>
>
>
> On Wednesday, September 10, 2014 5:16 AM, Sam Silvester <
> sam.silvester at gmail.com> wrote:
>
>
> Howdy,
>
> Can anybody shed any light on how the PEMs on a T4000 actually distribute
> power to each FPC slot?
>
> Have the case of a single FPC slot that is showing power being received
> from only one of the PEMs, whilst all the other FPC slots are load sharing
> as expected.
>
> Replacing the FPC shows the same issue, so we're pretty happy that it's
> "slot specific".
>
> What I'm curious about is if the midplane has individual 'traces' (for lack
> of a better term) for supplying power to each FPC from the two PEMs, or if
> there is a common bus shared between all the FPCs from each PEM. The reason
> I ask is if the PEM only has a single connection to the midplane, replacing
> it seems pointless and instead it looks like we're better off replacing the
> midplane. If the PEM has individual outputs to each slot, then replacing
> the PEM seems like a reasonable approach.
>
> I've been pointed at the following document (
>
> http://www.juniper.net/documentation/en_US/release-independent/junos/topics/concept/power-supply-t4000-description.html
> )
> which is very light-on in terms of detail. Does anybody know if there is a
> more detailed document available (or even internally?) that we can ask
> about?
>
> Thanks!