[outages] Comcast Bay Area: interruptions past few days
    joel jaeggli 
    joelja at bogus.com
       
    Tue Jan 26 02:20:51 EST 2016
    
    
  
On 1/25/16 5:51 PM, Jonathan Lassoff via Outages wrote:
> Good luck getting some resolution.
> 
> For what it's worth -- "Greak Oaks" refers to 11 Greak Oaks, a large
> Equinix facility in San Jose: https://beta.peeringdb.com/fac/6
SV1 and SV5 are part of that campus.
> Cheers,
> jof
> 
> On Mon, Jan 25, 2016 at 4:49 PM, Jeremy Chadwick via Outages
> <outages at outages.org> wrote:
>> For the past few days I've seen what may be a layer 1 problem between
>> two of Comcast's locations: Sunnyvale, CA and "Great Oaks", CA (not sure
>> if this is a street, town, or what).
>>
>> Was hoping John Neiberger et al might be able to look into this.
>>
>> Timestamps and durations are below, with the relevant mtr data included
>> as well.  Sadly, due to a DNS mistake in my mtr configs, I don't have
>> return-path (VPS --> Comcast) mtrs.  I've since fixed this mistake, so
>> If it happens again I'll have them from both directions.
only two of your traceroutes record loss cascading to the endpoint...
intermediate loss in a traceroute isn't very interesting unless it also
appears on subsequent hops otherwise you're just testing the control-planes.
>> I'll also note that the intermittent packet loss + latency seen at
>> hop #5 is normal -- I see this even when things are working just fine.
>> It's almost certainly ICMP prio, no biggie.
>>
>> #1 -- January 19, 13:17 to 13:20 PST (UTC-8) (~3 minutes)
>> #2 -- January 19, 22:30 to 22:33 PST (UTC-8) (~3 minutes)
>> #3 -- January 25, 14:30 to 14:35 PST (UTC-8) (~5 minutes)
>>
>> For all data shown: src = 69.181.142.213, dst = 104.238.183.73
>>
>> Data #1:
>>
>> === Tue Jan 19 13:16:00 PST 2016  (1453238160)
>> Start: Tue Jan 19 13:16:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.2   0.2   0.2   0.4
>>   2.|-- 69.181.136.1                                                      0.0%    30    30   9.6  16.8   9.6  39.4
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  11.5  18.1  10.1  86.1
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  15.9  17.7   9.8  54.1
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)        0.0%    30    30  18.4  24.7   9.6 114.9
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  15.6  18.5  11.4  35.3
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  11.5  19.2  11.3  78.0
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  28.8  21.2  11.7  57.5
>>   9.|-- xe-1-0-1.sjc20.ip4.gtt.net (89.149.184.250)                       0.0%    30    30  17.6  19.3  11.3  52.3
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  21.0  17.3  11.4  24.8
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  93.9  23.1  11.8  97.4
>> === END
>>
>> === Tue Jan 19 13:17:00 PST 2016  (1453238220)
>> Start: Tue Jan 19 13:17:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30   9.9  14.7   9.1  21.0
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  15.1  16.1   9.8  44.7
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  16.8  15.8   9.3  43.2
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)     40.0%    30    18  11.6  64.8  11.2 406.3
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Tue Jan 19 13:18:00 PST 2016  (1453238280)
>> Start: Tue Jan 19 13:18:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.2   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  21.5  13.7   8.9  21.5
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  12.9  13.5   9.0  19.5
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30   9.0  13.8   9.0  19.6
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)      0.0%    30    30  36.7  14.7   9.5  36.7
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Tue Jan 19 13:19:00 PST 2016  (1453238340)
>> Start: Tue Jan 19 13:19:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.2   0.2   0.4
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  16.8  19.7   9.1 111.4
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  12.4  18.1   9.6  95.8
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  13.7  14.8  10.0  26.1
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)      0.0%    30    30  14.5  14.4   9.5  22.6
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Tue Jan 19 13:20:00 PST 2016  (1453238400)
>> Start: Tue Jan 19 13:20:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.2   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  57.6  15.6   9.5  57.6
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  18.1  19.0   9.3  80.9
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  12.4  14.7   9.2  55.8
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       20.0%    30    24  10.3 701.5   9.9 2105.7
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  13.3  18.3  11.9  54.4
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  11.7  20.5  11.0  91.0
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  15.3  17.0  11.1  37.4
>>   9.|-- xe-1-0-1.sjc20.ip4.gtt.net (89.149.184.250)                       0.0%    30    30  12.9  16.0  11.2  32.8
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  16.9  17.5  11.7  29.0
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  16.8  17.1  11.1  27.3
>> === END
>>
>>
>> Data #2:
>>
>> === Tue Jan 19 22:29:00 PST 2016  (1453271340)
>> Start: Tue Jan 19 22:29:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.2   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30   8.8  13.7   8.7  28.4
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  10.7  13.9   9.4  32.6
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  65.9  15.8   9.7  65.9
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       26.7%    30    22 8344. 10013 8097. 11372.1
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  15.3  19.0  12.2  83.3
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  17.5  16.5  11.5  21.8
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  17.3  18.9  13.3  28.4
>>   9.|-- xe-1-1-2.sjc20.ip4.gtt.net (89.149.184.246)                       0.0%    30    30  22.0  18.7  14.5  26.0
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  18.7  19.5  13.6  40.2
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  20.7  21.4  13.3  91.0
>> === END
>>
>> === Tue Jan 19 22:30:00 PST 2016  (1453271400)
>> Start: Tue Jan 19 22:30:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.2   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  16.2  16.4   9.7  50.5
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  11.6  15.0   9.2  74.6
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  11.0  14.1   9.4  34.7
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)      6.7%    30    28 6042. 5278. 4875. 6044.0
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Tue Jan 19 22:31:00 PST 2016  (1453271460)
>> Start: Tue Jan 19 22:31:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  42.3  17.0   9.5  60.0
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  17.7  18.6   9.9  81.3
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  12.7  14.8   9.2  39.2
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)     56.7%    30    13 114.9  49.6   9.3 199.0
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Tue Jan 19 22:32:00 PST 2016  (1453271520)
>> Start: Tue Jan 19 22:32:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  12.1  16.5   8.9  57.1
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  11.0  15.0   9.5  53.6
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  13.2  14.0   9.4  33.6
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       43.3%    30    17 132.7  25.9   9.2 132.7
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)     93.3%    30     2  20.5  17.3  14.2  20.5
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238) 93.3%    30     2  19.9  16.0  12.0  19.9
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                          93.3%    30     2  13.4  13.5  13.4  13.7
>>   9.|-- xe-1-1-2.sjc20.ip4.gtt.net (89.149.184.246)                      93.3%    30     2  15.4  14.4  13.4  15.4
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)       93.3%    30     2  12.8  17.2  12.8  21.7
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                93.3%    30     2  12.9  12.8  12.7  12.9
>> === END
>>
>> === Tue Jan 19 22:33:00 PST 2016  (1453271580)
>> Start: Tue Jan 19 22:33:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  16.9  16.1   9.6  71.2
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  12.3  15.0   9.4  52.6
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  14.5  14.3   9.2  35.6
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       56.7%    30    13 13553 11910 9297. 13553.6
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  12.8  17.4  11.3  26.6
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  11.6  16.7  11.6  29.0
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  12.3  17.9  11.4  54.7
>>   9.|-- xe-1-0-1.sjc20.ip4.gtt.net (89.149.184.250)                       0.0%    30    30  18.4  16.7  11.2  35.0
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  13.7  16.9  12.0  26.8
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  17.6  18.7  12.3  64.6
>> === END
>>
>>
>> Data #3:
>>
>> === Mon Jan 25 14:30:00 PST 2016  (1453761000)
>> Start: Mon Jan 25 14:30:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  14.7  13.7   8.4  23.3
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  10.1  16.6   9.2 100.5
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  15.3  15.1   9.1  38.5
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       10.0%    30    27  10.7 355.4   9.4 1251.7
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  18.5  17.7  11.7  31.3
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  13.4  17.9  11.1  68.7
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  14.1  15.8  10.5  56.3
>>   9.|-- xe-1-1-2.sjc20.ip4.gtt.net (89.149.184.246)                       0.0%    30    30  14.6  15.0  11.0  20.9
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  19.6  15.2  10.9  21.0
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  16.5  16.1  11.1  41.9
>> === END
>>
>> === Mon Jan 25 14:31:00 PST 2016  (1453761060)
>> Start: Mon Jan 25 14:31:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.3   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  14.9  15.0   8.9  56.8
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  11.0  14.4   9.1  23.2
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  16.9  16.3   9.1  89.2
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)     10.0%    30    27  13.0  15.9   9.1  45.8
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Mon Jan 25 14:32:00 PST 2016  (1453761120)
>> Start: Mon Jan 25 14:32:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.2   0.2   0.4
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  17.1  13.7   9.3  31.9
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30  12.7  14.9   9.1  46.5
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  19.0  16.6   8.9  93.7
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)     10.0%    30    27  12.0  17.7   9.3 101.0
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Mon Jan 25 14:33:00 PST 2016  (1453761180)
>> Start: Mon Jan 25 14:33:00 2016
>> HOST: icarus.home.lan                                                Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                       0.0%    30    30   0.3   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                    0.0%    30    30  10.2  23.7   8.6 121.1
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)  0.0%    30    30   9.7  15.7   9.4  62.2
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)  0.0%    30    30  16.4  14.1   9.6  21.0
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)      0.0%    30    30  12.0  43.9   9.8 423.8
>>   6.|-- ???                                                            100.0    30     0   0.0   0.0   0.0   0.0
>> === END
>>
>> === Mon Jan 25 14:34:00 PST 2016  (1453761240)
>> Start: Mon Jan 25 14:34:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.3   0.2   0.2   0.4
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  12.0  14.4   8.7  57.1
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  10.5  15.8   9.4  80.0
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  13.7  14.5   9.2  23.3
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)        0.0%    30    30 166.4  31.3   9.2 166.4
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)     83.3%    30     5  17.6  17.4  16.4  18.7
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238) 83.3%    30     5  11.6  14.9  11.6  19.6
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                          80.0%    30     6  17.2  20.5  17.2  26.2
>>   9.|-- xe-1-1-2.sjc20.ip4.gtt.net (89.149.184.246)                      80.0%    30     6  12.8  15.0  12.8  20.9
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)       80.0%    30     6  19.0  16.9  15.1  19.4
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                80.0%    30     6  12.5  15.8  11.4  20.7
>> === END
>>
>> === Mon Jan 25 14:35:00 PST 2016  (1453761300)
>> Start: Mon Jan 25 14:35:00 2016
>> HOST: icarus.home.lan                                                  Loss%   Snt   Rcv  Last   Avg  Best  Wrst
>>   1.|-- gw.home.lan (192.168.1.1)                                         0.0%    30    30   0.2   0.2   0.2   0.3
>>   2.|-- 69.181.136.1                                                      0.0%    30    30  22.9  18.4   8.9  93.2
>>   3.|-- te-0-2-0-5-sur03.santaclara.ca.sfba.comcast.net (68.86.249.69)    0.0%    30    30  11.2  13.3   9.5  19.1
>>   4.|-- hu-0-3-0-4-ar01.santaclara.ca.sfba.comcast.net (68.87.192.177)    0.0%    30    30  16.2  14.0   9.0  46.1
>>   5.|-- be-33651-cr01.sunnyvale.ca.ibone.comcast.net (68.86.90.93)       26.7%    30    22 1776. 3705. 1776. 4921.8
>>   6.|-- be-10925-cr01.9greatoaks.ca.ibone.comcast.net (68.86.87.158)      0.0%    30    30  19.3  19.6  11.2  73.6
>>   7.|-- hu-0-11-0-0-pe03.11greatoaks.ca.ibone.comcast.net (68.86.85.238)  0.0%    30    30  17.0  15.0  10.9  25.1
>>   8.|-- ae12.sjc12.ip4.gtt.net (173.205.58.169)                           0.0%    30    30  18.0  15.9  10.9  41.0
>>   9.|-- xe-1-1-2.sjc20.ip4.gtt.net (89.149.184.246)                       0.0%    30    30  14.3  18.4  10.6  79.6
>>  10.|-- as20473.xe-1-2-3.cr1.sjc2.us.as4436.gtt.net (69.22.130.90)        0.0%    30    30  19.0  17.8  11.1  72.5
>>  11.|-- ???                                                              100.0    30     0   0.0   0.0   0.0   0.0
>>  12.|-- mambo.koitsu.org (104.238.183.73)                                 0.0%    30    30  20.1  15.9  11.3  22.8
>> === END
>>
>> --
>> | Jeremy Chadwick                                   jdc at koitsu.org |
>> | UNIX Systems Administrator                http://jdc.koitsu.org/ |
>> | Making life hard for others since 1977.             PGP 4BD6C0CB |
>>
>> _______________________________________________
>> Outages mailing list
>> Outages at outages.org
>> https://puck.nether.net/mailman/listinfo/outages
> _______________________________________________
> Outages mailing list
> Outages at outages.org
> https://puck.nether.net/mailman/listinfo/outages
> 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: signature.asc
Type: application/pgp-signature
Size: 229 bytes
Desc: OpenPGP digital signature
URL: <https://puck.nether.net/pipermail/outages/attachments/20160125/8b2944d4/attachment.sig>
    
    
More information about the Outages
mailing list