You are entitled to your opinion.

-John

================

> Agreed
> But the 7:1 guys are correct  Nowhere in the thread has anyone suggested
> applying 120vrms/60Hz to a 400 Hz variac.  The 7:1 factor is the required
> de-rating needed to operated a 400 Hz variac on 60 Hz in order to avoid
> core saturation.
>
>
>
> --- On Mon, 7/18/11, J. Forster <jfor at quik.com> wrote:
>
> From: J. Forster <jfor at quik.com>
> Subject: Re: [Boatanchors] Are 400 Hz variac's good for anything but a
> real      'boat anchor'
> To: "Bruce Long" <coolbrucelong at yahoo.com>
> Cc: "Bill L''Fuqua" <wlfuqu00 at uky.edu>, doc at kd4e.com, "John Hurst"
> <hurstjsj at verizon.net>, "'Boatanchors List'" <boatanchors at puck.nether.net>
> Date: Monday, July 18, 2011, 10:58 AM
>
> The statement is true. In a properly designed 400 Hz transformer operating
> at the rated voltage, the iron is not being saturated during any part of
> the cycle.
>
> If you go to 60 Hz with the same applied voltage, the iron will be
> hopelessly saturated, and it's incremental permeability will drop to near
> that of free space. It's like the iron just vanished.
>
> The magnetizing current will go up far, far more tha 7x.
>
> Best,
>
> -John
>
> =================
>
>
>> "The magnetizing current @60 Hz will *much* higher than 7 times the
>> current
>> at 400Hz."
>>
>> Please explain- justify.
>>
>> I agree with the 7:1 guys on this. 
>>
>> Basically the issue arises in the electronic speed/torque control of
>> induction motors.    Bruce   KJ3Z
>>
>
>
>