On 06.06.2005 18:15 Brad Swanson wrote
> Consider a 45k square foot data center with standard 19" racks with
> structured cabling and standard aisle cooling techniques. We use 6509's
> non-NEBS and have noticed the temp with the sup720's running (of course)
> hotter then the older sup2's. No minor/major alarms (within 5C degrees of
> minor in some cases), but have other folks used the NEBS chassis as a
> standard to get the front/back cooling as opposed to the right/left?
>
I see
active Sup720 standby Sup720
Intake 25.00/24.99/25.00 23.83/23.87/24.00
Exhaust 27.80/27.89/28.00 24.87/24.78/26.00
Intake 21.00/21.00/21.00 20.00/20.00/21.00
Exhaust 27.00/27.00/27.00 25.00/24.81/25.00
Intake 20.38/19.64/21.00 20.00/19.42/21.00
Exhaust 26.52/25.94/27.00 24.13/23.52/25.00
Temperature is current/average/maximum on weekly basis at different
Cat6509-NEB-A and different colocation centers.