>Can someone give me a quick real world lesson on power supplies for the
>7600/6500's?
>
>Looking at Cisco's site it seems that most of the AC supplies will run
>on 110 or 220 volts, with the capacity being halved at 110V.
>
>I'm planning on using a 7606 with a Sup720-3BXL, with maybe a couple
>line-cards to start. I won't be doing any POE and probably never will at
>this location. I'd like to do redundant supplies.
>
>What capacity power supplies should I be looking at? Can I reasonably
>stay at 110V, since it's a lot easier to get in most colo facilities? Is
>there a could rule of thumb for figuring this out?
Each card has a power budget. Figure out how much power you need,
then make sure either of your two power supplies alone can provide
it. Here are two snippets. One from a 110V source and another at 208V
both with 2500W power supplies. You will need the 2nd generation FAN2
fan shelf which moves more air and uses more power too with the
Sup720. At 110V with 2500W power supplies, there isn't a lot of power
if you have many high power usage line cards, but you can fit four of
the WS-X6348-RJ-45 cards in my 110V config below. You can always
start with 110V and change to 208V in the future. You can swap the
power cords one at a time while the router is running. One P/S can be
fed via 208V while the other P/S is fed via 110V while you upgrade.
The system will always reserve power for a redundant Sup whether it
is present or not. I don't know if this feature can be turned off.
-Robert
core3.tdc.nwt#sho power
system power redundancy mode = redundant
system power total = 2331.00 Watts (55.50 Amps @ 42V)
system power used = 857.64 Watts (20.42 Amps @ 42V)
system power available = 1473.36 Watts (35.08 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-2500W 2331.00 55.50 OK OK on
2 WS-CAC-2500W 2331.00 55.50 OK OK on
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
4 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
6 (Redundant Sup) - - 328.44 7.82 - -
core2.tlh.nyc#sho power
system power redundancy mode = redundant
system power total = 1153.32 Watts (27.46 Amps @ 42V)
system power used = 791.70 Watts (18.85 Amps @ 42V)
system power available = 361.62 Watts ( 8.61 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
2 WS-CAC-2500W 1153.32 27.46 OK OK on
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6348-RJ-45 100.38 2.39 100.38 2.39 on on
5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
6 (Redundant Sup) - - 328.44 7.82 - -
Inline Inline Inline Inline
Pwr-Requested Pwr-Allocated Local-Pwr-Pool Power
Slot Card-Type Watts A @42V Watts A @42V Watts A @42V Status
---- ------------------ ------- ------ ------- ------ ------- ------ ----------
1 WS-F6K-PWR - - - - 34.44 0.82 On
Tellurian Networks - Global Hosting Solutions Since 1995
http://www.tellurian.com | 888-TELLURIAN | 973-300-9211
"Well done is better than well said." - Benjamin Franklin