[c-nsp] C7600 power allocation
Harald Firing Karlsen
maillist at thelan.no
Mon Mar 30 10:10:39 EDT 2009
Alexandre Snarskii wrote:
> On Mon, Mar 30, 2009 at 11:51:43AM +0300, Dmitry Kiselev wrote:
>
>> Hello!
>>
>> Could anybody explain me how exactly IOS choise which module to
>> disable if system run in combined power mode and one of power inputs
>> failed?
>>
>>
>> http://www.cisco.com/en/US/docs/routers/7600/ios/12.2SR/configuration/guide/pwr_envr.html#wp1020384
>>
>> However, if one power supply fails and there is not enough power
>> for all of the previously powered-up modules, the system powers
>> down those modules.
>>
>>
>>
>> Could I do some pre-configuration to point IOS to modules "less
>> critical" for me?
>>
>
> As per this letter,
>
> http://puck.nether.net/pipermail/cisco-nsp/2006-March/028767.html
>
> you can achieve this placing less critical modules in highest
> numbered slots and more critical - to lowest.
>
Note however that the two SUP-slots got dedicated/reserved power, so
they will never shut down. That means if you only got one SUP you should
have a linecard in the other SUP-slot as well (as the power for this
slot is reserved anyway).
--