Example of lightly loaded 7609 running at 240v redundant with 3000watt supplies and sup720-3b. No POE.
 
edge#sh power
system power redundancy mode = redundant
system power total =     2771.16 Watts (65.98 Amps @ 42V)
system power used =      1636.74 Watts (38.97 Amps @ 42V)
system power available = 1134.42 Watts (27.01 Amps @ 42V)
                        Power-Capacity PS-Fan Output Oper
PS   Type               Watts   A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1    WS-CAC-3000W       2771.16 65.98  OK     OK     on
2    WS-CAC-3000W       2771.16 65.98  OK     OK     on
                        Pwr-Allocated  Oper
Fan  Type               Watts   A @42V State
---- ------------------ ------- ------ -----
1    FAN-MOD-09          241.50  5.75  OK
2    FAN-MOD-09          241.50  5.75  OK
                        Pwr-Requested  Pwr-Allocated  Admin Oper
Slot Card-Type          Watts   A @42V Watts   A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1    7600-SIP-200        240.24  5.72   240.24  5.72  on    on
2    7600-SIP-400        265.02  6.31   265.02  6.31  on    on
4    WS-X6408A-GBIC       84.00  2.00    84.00  2.00  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on

--- On Tue, 5/26/09, Bill Blackford <BBlackford at nwresd.k12.or.us> wrote:


From: Bill Blackford <BBlackford at nwresd.k12.or.us>
Subject: [c-nsp] Cat 6509 Power supplies
To: "cisco-nsp at puck.nether.net" <cisco-nsp at puck.nether.net>
Date: Tuesday, May 26, 2009, 10:51 AM


I have a question about power supplies.

I am upgrading a 6509 chassis from SuP1/MFSC2 to a pair of SUP720-3BXL's, fan and new power supplies. I originally spec'd a pair of 4000W units. Now as we know, these can only support NEMA L6-30, vs. the variable power supplies such as the 3000W. I've run out of L6-30R's in my data center as our new rack PDU's are of this spec. I may need to use 110V NEMA 5-20 plugs.

Can the 3000W power supply (in redundant mode) support a fully populated 6509 chassis (no POE) when using 110VAC?

Thanks



--
Bill Blackford                     
Senior Network Engineer            
Technology Systems Group           
Northwest Regional ESD             

my /home away from home