> Has anyone looked at using outside air to provide data center
> cooling during the winter season ?
> I am aware of Google and Intel research into
> this area but how about on a smaller scale ?
> How about raising ambient
> temperatures as well - do you keep your data centers at 65 or 80 ?
We do this and we have had mixed success. We have Liebert A/C units
which have something they call an "economizer." Essentially, when the
outside temperature falls below a certain point as measured by a simple
thermostat, the A/C unit moves a damper and instead of sucking hot air
from the room to cool, it sucks cold air from the outside, filters it,
and blows it in. At the same time, it turns off the compressor (because
the air is, in theory, already cold).
In the sales presentations and talking to A/C gurus, it all sounded very
smart and economical, but we've found that the actual management of the
damper and the temperature that it shifts are very delicate settings.
Depending on the time of the day (i.e., is there sunlight on that side
of the building or not?) and the season of the year (i.e., is this just
a little cold snap or an extended period?), as well as the outside
humidity level (is it very different from the humidity in the room or
not?), the temperature has to be adjusted a bit in each direction. Our
units don't have a computer control for that, so that means someone goes
out every few weeks with a screwdriver and manually fiddles the
economizer thermostat settings.
We can compensate a bit on the computer control side by changing the the
system thermostat around a few degrees, but there is no direct linkage
between the economizer part of the system--it's completely independent,
essentially an add-on--and the rest of the cooling system.
I honestly can't tell whether we are saving any money on this or not,
but for our latitude and climate, I would not recommend it to anyone
else. We have had to replace the thermostats and damper controllers,
and that eats up $300 to $500 for every service call. Plus, while we
were learning about it, we had some midnight room-got-too-hot moments,
which also cost us.
I think that if you lived someplace where it was in the 5C/40F range or
below day-round for weeks at a time, this would probably work (assuming
that you have physical ability to install this kind of unit). In our
climate, where it is 5C/40F for 8 hours at night and 20C/70F the rest of
the day, for our 3 month winter, it was probably not the right decision.
jms
--