[c-nsp] Power Supply 2 ouput has dropped

quinn snyder snyderq at gmail.com
Fri Jan 4 15:24:08 EST 2013


what version of code are you running?  
i ran into something similar with c6509 running sxj.  something to do with an invalid pointer or something during the sharing of values between the peers.  power supplies were 3kw powered by 240v pdu's off a 415v buss.  even during proper operation of the pdu -- confirmed with a multimeter for current and voltage -- the p/s would show ~ ½ available power.

eventually upgrading to a later sxj release fixed the issue.  cisco has a posted ddts -- internally at last check -- for this.  hit up your account team for details.

regards,
q.

--  
quinn snyder
snyderq at gmail.com


On Friday, 4 January 2013 at 12:23 PM, Farooq Razzaque wrote:

>  
>  
>  
> Hi  
>  
>  
>  
> I m getting the following power supply error frequently on 6513 switches operating in VSS mode. It seems to be the issue with the input of power supply 2.
>  
> Below are the ouput of the show environment and show power .
>  
>  
> Anyone has experience this before
>  
>  
>  
> 83559233: Dec 12 09:37:55.985 UAE: vs_raised_alarm_to_cardstate(): NULL threshold info for switch 1 power-supply 2 power-output-mode violation
> 83559234: Dec 12 09:37:55.949 UAE: %C6KPWR-SW1_SP-4-PSOUTPUTDROP: Power supply 2 output has dropped
>  
>  
> 83559235: Dec 12 09:37:55.949 UAE:
>  
>  
>  
> %C6KPWR-SW1_SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 2671.20W
>  
> 83559236: Dec 12 09:37:55.989 UAE: %C6KPWR-SW1_SP-4-PSREDUNDANTMISMATCH: power supplies rated outputs do not match.
> 83559237: Dec 12 09:37:55.989 UAE: %C6KPWR-SW1_SP-4-PSNOREDUNDANCY: Power supplies are not in full redundancy, power usage exceeds lower capacity supply
>  
>    
> 83559238: Dec 12 09:37:57.997 UAE: %C6KPWR-SW1_SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 5771.64W
> 83559239: Dec 12 09:37:58.001 UAE: %C6KPWR-SW1_SP-4-PSREDUNDANTBOTHSUPPLY: in power-redundancy mode, system is operating on both power supplies
>  
>  
> .
>  
>  
> 83559240: Dec 12 09:38:02.084 UAE: vs_raised_alarm_to_cardstate(): NULL threshold info for switch 1 power-supply 2 power-output-mode violation
>  
>  
> 83559241: Dec 12 09:38:02.045 UAE: %C6KPWR-SW1_SP-4-PSOUTPUTDROP: Power supply 2 output has dropped
> 83559242: Dec 12 09:38:02.045 UAE: %C6KPWR-SW1_SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 2671.20W
> 83559243: Dec 12 09:38:02.089 UAE: %C6KPWR-SW1_SP-4-PSREDUNDANTMISMATCH: power supplies rated outputs do not match.
> 83559244: Dec 12 09:38:02.093 UAE: %C6KPWR-SW1_SP-4-PSNOREDUNDANCY: Power supplies are not in full redundancy, power usage exceeds lower capacity supply
>  
>  
> 83559245: Dec 12 09:38:04.112 UAE: %C6KPWR-SW1_SP-4-INPUTCHANGE: Power supply 2 input has changed. Power capacity adjusted to 5771.64W
>  
>  
> 83559246: Dec 12 09:38:04.112 UAE: %C6KPWR-SW1_SP-4-PSREDUNDANTBOTHSUPPLY: in power-redundancy mode, system is operating on both power supplies.
>  
>  
> SW01# sh environment switch 1 status power-supply 2
> switch 1 power-supply 2:  
> switch 1 power-supply 2 fan-fail: OK
> switch 1 power-supply 2 power-input: AC low  
> switch 1 power-supply 2 power-output-mode: low
> switch 1 power-supply 2 power-output-fail: OK  
>  
>  
> SW01#sh power system  
> power redundancy mode = redundant
> system power redundancy operationally = non-redundant
> system power total = 5771.64 Watts (137.42 Amps @ 42V)
> system power used = 3451.56 Watts (82.18 Amps @ 42V)
> system power available = 2320.08 Watts (55.24 Amps @ 42V)
> Power-Capacity PS-Fan Output Oper
> PS Type Watts A @42V Status Status State
> ---- ------------------ ------- ------ ------ ------ -----
> 1 WS-CAC-6000W 5771.64 137.42 OK OK on  
>  
>  
> 2 WS-CAC-6000W 2671.20 63.60 OK OK on
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
>  
> SW01# sh environment switch 1 status power-supply 2
>  
> switch 1 power-supply 2 fan-fail: OKswitch 1 power-supply 2: fan-fail: OK
> switch 1 power-supply 2 power-input: AC high  
> switch 1 power-supply 2 power-output-mode: high
> switch 1 power-supply 2 power-output-fail: OK
>  
>    
> SW01#sh power  
> system power redundancy mode = redundant
> system power total = 5771.64 Watts (137.42 Amps @ 42V)
> system power used = 3451.56 Watts (82.18 Amps @ 42V)
> system power available = 2320.08 Watts (55.24 Amps @ 42V)
> Power-Capacity PS-Fan Output Oper
> PS Type Watts A @42V Status Status State
> ---- ------------------ ------- ------ ------ ------ -----
>  
> 1 WS-CAC-6000W 5771.64 137.42 OK OK on  
> 2 WS-CAC-6000W 5771.64 137.42 OK OK on  
>  
>  
> _______________________________________________
> cisco-nsp mailing list cisco-nsp at puck.nether.net (mailto:cisco-nsp at puck.nether.net)
> https://puck.nether.net/mailman/listinfo/cisco-nsp
> archive at http://puck.nether.net/pipermail/cisco-nsp/






More information about the cisco-nsp mailing list