[outages] Level 3 fiber cut San Bernardino, CA
    Brian Knight 
    ml at knight-networks.com
       
    Wed Oct 24 22:28:10 EDT 2018
    
    
  
This was resolved as of 6:09pm CT.  Both of our links are back up and 
running with no further problems.
-Brian
On 2018-10-24 13:06, Brian Knight via Outages wrote:
> We've heard that splicing has been going on for the past several hours
> on the 264-count cable.  Estimated time to finish that splice is 20:00
> GMT.
> 
> -Brian
> 
> On 2018-10-24 07:43, Brian Knight via Outages wrote:
>> Got a Level 3 fiber cut in San Bernardino, CA going on for about 17
>> hours now.  Our first link alarm was at 3:47pm CT yesterday.  $DAYJOB
>> has two 1G circuits affected.
>> 
>> Looks like they had a hell of a time getting the replacement cable and
>> splice conduit installed.  Splicing is estimated to start in another
>> 2.5-3.5 hours on the east side of the cut.
>> 
>> Here's the latest we received from Level 3.
>> 
>> 
>> 10/24/2018 12:29:56 GMT -
>> *** CASCADED EXTERNAL NOTES 24-Oct-2018 12:22:53 GMT From CASE: 
>> 15371425 - Event
>> The Outside Plant Engineer has reported that cable preparations on
>> both the west side and the east side of the cable is ongoing. It is
>> estimated splicing on the west side will begin at 14:00 GMT and
>> splicing on the east side will begin between 15:00 GMT and 16:00 GMT.
>> 
>> 
>> 10/24/2018 11:10:34 GMT -
>> *** CASCADED EXTERNAL NOTES 24-Oct-2018 11:04:06 GMT From CASE: 
>> 15371425 - Event
>> The Outside Plant Engineer has confirmed the trench is dug and the
>> replacement cable is being ran between manholes at the west side of
>> the damage. Preparations are complete at the east side and splicing
>> expected to begin at 11:30 GMT with the 264 count cable, then the 84
>> count cable followed by a 60 count lateral cable. Restoration efforts
>> are ongoing with an ETTR that remains unchanged, 17:30 GMT.
>> 
>> 
>> 10/24/2018 10:05:30 GMT -
>> *** CASCADED EXTERNAL NOTES 24-Oct-2018 09:58:52 GMT From CASE: 
>> 15371425 - Event
>> The Outside Plant Engineer reported the replacement section of cable
>> got stuck when pulling it into position. A second splice enclosure
>> will be installed in the next manhole. Field Operations will dig a
>> trench between the two enclosures to complete the installation of the
>> 2,400 foot section of 264 count replacement cable. The trench is
>> expected to be complete at approximately 10:30 GMT with an estimated
>> time splicing will begin of 12:30 GMT.
>> 
>> 
>> 10/24/2018 08:08:37 GMT -
>> *** CASCADED EXTERNAL NOTES 24-Oct-2018 08:01:50 GMT From CASE: 
>> 15371425 - Event
>> The Outside Plant Engineer reported the replacement section of fiber
>> cable has arrived and is currently being pulled into position. Along
>> with the section of fiber cable, a new splice enclosure is being
>> prepped and will be replaced to complete repairs of the 264 count
>> cable. The 84 count cable has been prepped and ready for splicing.
>> Field Operations have moved to an adjacent manhole looking for
>> available slack to repair to the 168 count cable. The Outside Plant
>> Engineer reported splicing is expected to commence at 10:00 GMT. The
>> next update will be sent at that time or if additional information is
>> received.
>> 
>> 
>> -Brian
    
    
More information about the Outages
mailing list