[c-nsp] 6500/7600 "reserved" power for secondary sups
Ian Cox
icox at cisco.com
Fri Mar 3 16:19:06 EST 2006
At 03:28 PM 3/3/2006 -0500, Richard A Steenbergen wrote:
>Hello,
>
>Is there a way to disable the automatically reserved power for a secondary
>supervisor on the 6500/7600s? For example:
No.
>system power redundancy mode = redundant
>system power total = 2331.00 Watts (55.50 Amps @ 42V)
>system power used = 1280.53 Watts (30.49 Amps @ 42V)
>system power available = 1050.47 Watts (25.01 Amps @ 42V)
> Power-Capacity PS-Fan Output Oper
>PS Type Watts A @42V Status Status State
>---- ------------------ ------- ------ ------ ------ -----
>1 WS-CAC-2500W 2331.00 55.50 OK OK on
>2 WS-CAC-2500W 2331.00 55.50 OK OK on
> Pwr-Requested Pwr-Allocated Admin Oper
>Slot Card-Type Watts A @42V Watts A @42V State State
>---- ------------------ ------- ------ ------- ------ ----- -----
>1 WS-X6704-10GE 295.26 7.03 295.26 7.03 on on
>3 WS-X6748-SFP 328.44 7.82 328.44 7.82 on on
>5 WS-SUP720-3BXL 328.44 7.82 328.44 7.82 on on
>6 (Redundant Sup) - - 328.44 7.82 - -
>
>Under slot 6, the system is reserving power for 328.44 watts (the same as
>the primary sup720-3bxl), but there is no card in slot 6, nor has there
>ever been.
This is by design. We need to be able to handle the case of plugging
in a redundant supervisor and having it power up. You can place your
line card into the redundant supervisor slot.
Ian
>--
>Richard A Steenbergen <ras at e-gerbil.net> http://www.e-gerbil.net/ras
>GPG Key ID: 0xF8B12CBC (7535 7F59 8204 ED1F CC1C 53AF 4C41 5ECA F8B1 2CBC)
>_______________________________________________
>cisco-nsp mailing list cisco-nsp at puck.nether.net
>https://puck.nether.net/mailman/listinfo/cisco-nsp
>archive at http://puck.nether.net/pipermail/cisco-nsp/
More information about the cisco-nsp
mailing list